Refrigeration & Air Conditioning Mechanic Red Seal · Question
A residential split air conditioning system containing R-410A is found to be 2.5 kg undercharged from its nominal 5.0 kg charge. What is the recommended method for adding refrigerant to ensure proper system performance and oil return?
R-410A is a zeotropic blend, and to maintain its composition, it must be charged as a liquid. Charging it into the low-pressure side as a liquid is acceptable,
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
Question: A residential split air conditioning system containing R-410A is found to be 2.5 kg undercharged from its nominal 5.0 kg charge. What is the recommended method for adding refrigerant to ensure proper system performance and oil return?
Answer options:
- Add refrigerant as a vapour to the low-pressure side until the charge is correct.
- Add refrigerant as a liquid to the high-pressure side during operation. ✅ Add refrigerant as a liquid to the low-pressure side slowly, ensuring it flashes to vapour before entering the compressor.
- Add refrigerant as a liquid to the suction line while the compressor is off, then start the system.
Correct answer: Add refrigerant as a liquid to the low-pressure side slowly, ensuring it flashes to vapour before entering the compressor.
Explanation: R-410A is a zeotropic blend, and to maintain its composition, it must be charged as a liquid. Charging it into the low-pressure side as a liquid is acceptable, provided it flashes to vapour before reaching the compressor to prevent liquid slugging and potential damage.
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
More about Refrigeration & Air Conditioning Mechanic Red Seal
Related Questions
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
- Which type of electric motor requires a capacitor for starting and running, offering higher efficiency and bet
- When evacuating a refrigeration system, what is the recommended deep vacuum level, typically measured in micro
More for Refrigeration & Air Conditioning Mechanic Red Seal candidates
FAQs
Question explanations
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.