A walk-in freezer operating on R-404A exhibits low box temperature, frosted suction line back to the compressor, and excessively high suction pressure. The TXV has a sensing bulb securely attached to the suction line. What is the most probable issue with the TXV setting?

Low superheat (overfeeding) means the valve is allowing too much liquid refrigerant into the evaporator, leading to a flooded evaporator, frosted suction line,

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A walk-in freezer operating on R-404A exhibits low box temperature, frosted suction line back to the compressor, and excessively high suction pressure. The TXV has a sensing bulb securely attached to the suction line. What is the most probable issue with the TXV setting?

Answer options:

  • The TXV is set for excessively high superheat. ✅ The TXV is set for excessively low superheat (overfeeding).
  • The TXV's equalizer line is plugged.
  • The TXV's sensing bulb has lost its charge.

Correct answer: The TXV is set for excessively low superheat (overfeeding).

Explanation: Low superheat (overfeeding) means the valve is allowing too much liquid refrigerant into the evaporator, leading to a flooded evaporator, frosted suction line, and high suction pressure.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.