While commissioning a new R-134a refrigeration system, the technician measures the evaporator outlet temperature at 5°C and the corresponding saturated suction temperature at -5°C. The condenser outlet temperature is 35°C and the saturated condensing temperature is 45°C. What are the superheat and subcooling values, respectively?

Superheat = Evaporator outlet temp - Saturated suction temp = 5°C - (-5°C) = 10 K. Subcooling = Saturated condensing temp - Condenser outlet temp = 45°C - 35°C

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: While commissioning a new R-134a refrigeration system, the technician measures the evaporator outlet temperature at 5°C and the corresponding saturated suction temperature at -5°C. The condenser outlet temperature is 35°C and the saturated condensing temperature is 45°C. What are the superheat and subcooling values, respectively?

Answer options: ✅ 10 K superheat, 10 K subcooling

  • 5 K superheat, 10 K subcooling
  • 10 K superheat, 5 K subcooling
  • 5 K superheat, 5 K subcooling

Correct answer: 10 K superheat, 10 K subcooling

Explanation: Superheat = Evaporator outlet temp - Saturated suction temp = 5°C - (-5°C) = 10 K. Subcooling = Saturated condensing temp - Condenser outlet temp = 45°C - 35°C = 10 K.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.