A refrigeration machinery room contains equipment with 75 kg of R-410A. According to CSA B52, what is the minimum required exhaust ventilation capacity in L/s for this room, assuming normal operation?

CSA B52 specifies a minimum general ventilation rate of 0.5 L/s per kilogram of refrigerant for machinery rooms. For 75 kg of R-410A, this equates to 75 kg * 0.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A refrigeration machinery room contains equipment with 75 kg of R-410A. According to CSA B52, what is the minimum required exhaust ventilation capacity in L/s for this room, assuming normal operation?

Answer options: ✅ 150 L/s

  • 75 L/s
  • 225 L/s
  • 300 L/s

Correct answer: 150 L/s

Explanation: CSA B52 specifies a minimum general ventilation rate of 0.5 L/s per kilogram of refrigerant for machinery rooms. For 75 kg of R-410A, this equates to 75 kg * 0.5 L/s/kg = 37.5 L/s. However, Section 7.2.1.2 mandates a minimum of 150 L/s for any machinery room.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.