Refrigeration & Air Conditioning Mechanic Red Seal · Question

A newly installed refrigeration system utilizing R-717 (ammonia) is being commissioned in a food processing facility. CSA B52 requires a refrigerant detection system to be installed in the machinery room. What is the maximum alarm setpoint for this detection system, as a percentage of the lower flammable limit (LFL)?

For Group 2 refrigerants like R-717, CSA B52 Section 8.11.3 requires that the alarm for the refrigerant detection system in a machinery room must be set to acti

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A newly installed refrigeration system utilizing R-717 (ammonia) is being commissioned in a food processing facility. CSA B52 requires a refrigerant detection system to be installed in the machinery room. What is the maximum alarm setpoint for this detection system, as a percentage of the lower flammable limit (LFL)?

Answer options: ✅ 10% LFL

  • 25% LFL
  • 50% LFL
  • 100% LFL

Correct answer: 10% LFL

Explanation: For Group 2 refrigerants like R-717, CSA B52 Section 8.11.3 requires that the alarm for the refrigerant detection system in a machinery room must be set to activate at a concentration not exceeding 10% of the lower flammable limit (LFL).

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.