A refrigeration system using 150 kg of R-290 (propane) is installed in a standalone machinery room. What is the minimum number of mechanical ventilation fan systems required by CSA B52 to ensure proper machinery room ventilation?

For machinery rooms containing refrigerants Group A3 or B3, or a charge exceeding 50 kg of Group A2, A2L, B2 or B2L, CSA B52 Section 7.2.1.3 requires two fan sy

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A refrigeration system using 150 kg of R-290 (propane) is installed in a standalone machinery room. What is the minimum number of mechanical ventilation fan systems required by CSA B52 to ensure proper machinery room ventilation?

Answer options:

  • One primary system with no backup. ✅ One primary system with a standby fan of equal capacity.
  • Two independent primary systems, each capable of full ventilation.
  • One primary system with a manual override to increase speed.

Correct answer: One primary system with a standby fan of equal capacity.

Explanation: For machinery rooms containing refrigerants Group A3 or B3, or a charge exceeding 50 kg of Group A2, A2L, B2 or B2L, CSA B52 Section 7.2.1.3 requires two fan systems, either two full-capacity fans or one full-capacity fan and one standby fan of equal capacity.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.