A refrigeration system operating with R-134a has a design pressure of 1800 kPa on the high side. According to CSA B52, what is the maximum permissible setting for the pressure relief valve (PRV) on this high-pressure side?

CSA B52 specifies that the pressure relief device shall be set to open at a pressure not exceeding the design pressure of the high side by more than 10%. Theref

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A refrigeration system operating with R-134a has a design pressure of 1800 kPa on the high side. According to CSA B52, what is the maximum permissible setting for the pressure relief valve (PRV) on this high-pressure side?

Answer options:

  • 1800 kPa ✅ 1980 kPa
  • 2070 kPa
  • 2160 kPa

Correct answer: 1980 kPa

Explanation: CSA B52 specifies that the pressure relief device shall be set to open at a pressure not exceeding the design pressure of the high side by more than 10%. Therefore, 1800 kPa * 1.10 = 1980 kPa.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.