Refrigeration & Air Conditioning Mechanic Red Seal · Question
A ruptured pressure relief valve on a large R-744 (CO₂) system in a machinery room discharges into the atmosphere. The relief capacity is 12 kg/min and the room volume is 80 m³. If the emergency ventilation system fails, how quickly could the CO₂ concentration reach a hazardous level (e.g., 5% by volume, which causes rapid breathing and symptoms)? (Assume uniform mixing, CO₂ density at STP = 1.98 kg/m³)
Target CO₂ volume = 80 m³ * 0.05 = 4 m³. Mass of CO₂ at 5% = 4 m³ * 1.98 kg/m³ = 7.92 kg. Time to reach hazardous level = 7.92 kg / (12 kg/min) ≈ 0.66 minutes,
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
Question: A ruptured pressure relief valve on a large R-744 (CO₂) system in a machinery room discharges into the atmosphere. The relief capacity is 12 kg/min and the room volume is 80 m³. If the emergency ventilation system fails, how quickly could the CO₂ concentration reach a hazardous level (e.g., 5% by volume, which causes rapid breathing and symptoms)? (Assume uniform mixing, CO₂ density at STP = 1.98 kg/m³)
Answer options:
- Less than 30 seconds ✅ Approximately 1 minute
- Approximately 5 minutes
- Over 10 minutes
Correct answer: Approximately 1 minute
Explanation: Target CO₂ volume = 80 m³ * 0.05 = 4 m³. Mass of CO₂ at 5% = 4 m³ * 1.98 kg/m³ = 7.92 kg. Time to reach hazardous level = 7.92 kg / (12 kg/min) ≈ 0.66 minutes, or approximately 40 seconds. This demonstrates rapid onset of oxygen displacement and health hazards. This highlights the dangers of CO2.
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
More about Refrigeration & Air Conditioning Mechanic Red Seal
Related Questions
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
- Which type of electric motor requires a capacitor for starting and running, offering higher efficiency and bet
- When evacuating a refrigeration system, what is the recommended deep vacuum level, typically measured in micro
More for Refrigeration & Air Conditioning Mechanic Red Seal candidates
FAQs
Question explanations
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.