A refrigeration unit's single-phase compressor motor draws 15.0 A at 240 V and has a power factor of 0.85 lagging when running. What is the approximate true power consumed by the motor?

True power (watts) = Voltage × Amperage × Power Factor (P = V × I × PF). So, P = 240 V × 15.0 A × 0.85 = 3060 W. This represents the actual work done by the mot

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A refrigeration unit's single-phase compressor motor draws 15.0 A at 240 V and has a power factor of 0.85 lagging when running. What is the approximate true power consumed by the motor?

Answer options: ✅ 3060 W

  • 3600 VA
  • 5196 W
  • 4248 VA

Correct answer: 3060 W

Explanation: True power (watts) = Voltage × Amperage × Power Factor (P = V × I × PF). So, P = 240 V × 15.0 A × 0.85 = 3060 W. This represents the actual work done by the motor.