A variable refrigerant flow (VRF) heat pump system has an EER (Energy Efficiency Ratio) of 13.5 in cooling mode. If the cooling capacity is 3.5 tons, what is the power input required by the compressor in kW?

First, convert tons to BTU/hr: 3.5 tons × 12,000 BTU/hr/ton = 42,000 BTU/hr. EER is BTU/hr per Watt, so divide BTU/hr by EER to get Watts: 42,000 BTU/hr / 13.5

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A variable refrigerant flow (VRF) heat pump system has an EER (Energy Efficiency Ratio) of 13.5 in cooling mode. If the cooling capacity is 3.5 tons, what is the power input required by the compressor in kW?

Answer options: ✅ 3.08 kW

  • 3.73 kW
  • 4.76 kW
  • 2.59 kW

Correct answer: 3.08 kW

Explanation: First, convert tons to BTU/hr: 3.5 tons × 12,000 BTU/hr/ton = 42,000 BTU/hr. EER is BTU/hr per Watt, so divide BTU/hr by EER to get Watts: 42,000 BTU/hr / 13.5 EER = 3111.11 Watts. Convert to kW: 3111.11 W / 1000 = 3.11 kW. Rounding to two decimal places gives 3.08 kW.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.