Electrician Red Seal · Question
A plant technician notices that the pressure reading on the HMI for a specific vessel is consistently 15 kPa lower than the local pressure gauge. The pressure transducer producing the 4-20 mA signal was recently replaced. What is the most probable cause of this discrepancy?
A consistent offset in a 4-20 mA signal usually points to a calibration issue, specifically the zero point or span calibration of the transducer itself. If the
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A plant technician notices that the pressure reading on the HMI for a specific vessel is consistently 15 kPa lower than the local pressure gauge. The pressure transducer producing the 4-20 mA signal was recently replaced. What is the most probable cause of this discrepancy?
Answer options:
- The HMI display resolution is too low.
- The PLC's analog input module is faulty. ✅ The transducer's calibration has drifted or its zero point was not correctly set.
- The communication cable between the PLC and HMI is damaged.
Correct answer: The transducer's calibration has drifted or its zero point was not correctly set.
Explanation: A consistent offset in a 4-20 mA signal usually points to a calibration issue, specifically the zero point or span calibration of the transducer itself. If the analog input module or communication cable were faulty, the readings would likely be erratic or absent, not consistently offset. Low HMI resolution would not cause a consistent offset.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.