Electrician Red Seal · Question
During the inspection of a recently installed conduit system, an inspector identifies that a section of flexible metal conduit (FMC) exceeds the maximum length permitted by the CEC. The FMC is being used for a motor connection. What is the maximum length of FMC generally permitted by the CEC for such applications in dry locations?
Rule 12-1006(6) of the CEC generally limits flexible metal conduit (FMC) to a maximum length of 1.2 m (4 ft) for connections to motors in dry locations. This ru
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: During the inspection of a recently installed conduit system, an inspector identifies that a section of flexible metal conduit (FMC) exceeds the maximum length permitted by the CEC. The FMC is being used for a motor connection. What is the maximum length of FMC generally permitted by the CEC for such applications in dry locations?
Answer options:
- 1.0 m (3.3 ft) ✅ 1.2 m (4 ft)
- 1.5 m (5 ft)
- 1.8 m (6 ft)
Correct answer: 1.2 m (4 ft)
Explanation: Rule 12-1006(6) of the CEC generally limits flexible metal conduit (FMC) to a maximum length of 1.2 m (4 ft) for connections to motors in dry locations. This rule ensures adequate protection and ease of replacement while limiting potential damage to conductors from excessive movement.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.