An electrician is installing rigid PVC conduit in an area exposed to direct sunlight in a dry location. The conduit will contain insulated conductors with a temperature rating of 75 °C. The maximum expected ambient temperature is 40 °C. What is the maximum percentage fill permitted for the conduit by the CEC?

Table 8, Note (1) of the CEC specifies that for three or more conductors in a raceway, the maximum fill percentage is 40%. However, Rule 12-902(b) permits a 53%

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is installing rigid PVC conduit in an area exposed to direct sunlight in a dry location. The conduit will contain insulated conductors with a temperature rating of 75 °C. The maximum expected ambient temperature is 40 °C. What is the maximum percentage fill permitted for the conduit by the CEC?

Answer options:

  • 30%
  • 40% ✅ 53%
  • 60%

Correct answer: 53%

Explanation: Table 8, Note (1) of the CEC specifies that for three or more conductors in a raceway, the maximum fill percentage is 40%. However, Rule 12-902(b) permits a 53% conduit fill if one conductor is installed, 31% for two conductors, and 40% for three or more conductors within a raceway. The question implies an unspecified number of conductors beyond just one, so the 53% applies to conductors of the same type and size, if only one conductor is installed.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.