Electrician Red Seal · Question
A service entrance conductor for a single-dwelling unit is to be sized. The calculated demand load for the dwelling is 100 A. The service conductors will be 75 °C rated copper. Considering Rule 4-004(1)(a) and Table 2, what is the minimum standard ampere rating of overcurrent protection required for this service?
For a dwelling unit, Rule 8-200 provides methods for calculating demand load. Once calculated, Rule 4-004(1)(a) permits the use of conductors with an ampacity n
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A service entrance conductor for a single-dwelling unit is to be sized. The calculated demand load for the dwelling is 100 A. The service conductors will be 75 °C rated copper. Considering Rule 4-004(1)(a) and Table 2, what is the minimum standard ampere rating of overcurrent protection required for this service?
Answer options:
- 80 A
- 90 A ✅ 100 A
- 125 A
Correct answer: 100 A
Explanation: For a dwelling unit, Rule 8-200 provides methods for calculating demand load. Once calculated, Rule 4-004(1)(a) permits the use of conductors with an ampacity no less than the calculated demand load when protected by an overcurrent device of the same rating, or the next standard overcurrent device rating if the calculated load falls between standard sizes. Since a 100 A demand load is a standard overcurrent device size, a 100 A overcurrent device is required, assuming appropriately sized 75 °C conductors from Table 2.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.