An industrial facility is being upgraded, and a new 400 A main service entrance conductor is to be installed. The conductors are 500 kcmil (MCM) copper, insulated with RW90, and installed in a single conduit. The ambient temperature is 30°C (86°F), and there are no more than 3 current-carrying conductors. Based on CEC Table 2, what is the maximum ampacity of these conductors after applying the appropriate correction factors?

According to CEC Table 2, a 500 kcmil copper conductor with 90°C (194°F) insulation has an ampacity of 435 A when not more than three conductors are in a condui

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An industrial facility is being upgraded, and a new 400 A main service entrance conductor is to be installed. The conductors are 500 kcmil (MCM) copper, insulated with RW90, and installed in a single conduit. The ambient temperature is 30°C (86°F), and there are no more than 3 current-carrying conductors. Based on CEC Table 2, what is the maximum ampacity of these conductors after applying the appropriate correction factors?

Answer options:

  • 380 A
  • 400 A ✅ 435 A
  • 455 A

Correct answer: 435 A

Explanation: According to CEC Table 2, a 500 kcmil copper conductor with 90°C (194°F) insulation has an ampacity of 435 A when not more than three conductors are in a conduit (Column 4). No adjustment factor for ambient temperature is needed as the temperature is 30°C (86°F).

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.