An industrial facility is being upgraded, and a new 400 A main service entrance conductor is to be installed. The conductors are 500 kcmil (MCM) copper, insulated with RW90, and installed in a single conduit. The ambient temperature is 30°C (86°F), and there are no more than 3 current-carrying conductors. Based on CEC Table 2, what is the maximum ampacity of these conductors after applying the appropriate correction factors?
According to CEC Table 2, a 500 kcmil copper conductor with 90°C (194°F) insulation has an ampacity of 435 A when not more than three conductors are in a condui
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An industrial facility is being upgraded, and a new 400 A main service entrance conductor is to be installed. The conductors are 500 kcmil (MCM) copper, insulated with RW90, and installed in a single conduit. The ambient temperature is 30°C (86°F), and there are no more than 3 current-carrying conductors. Based on CEC Table 2, what is the maximum ampacity of these conductors after applying the appropriate correction factors?
Answer options:
- 380 A
- 400 A ✅ 435 A
- 455 A
Correct answer: 435 A
Explanation: According to CEC Table 2, a 500 kcmil copper conductor with 90°C (194°F) insulation has an ampacity of 435 A when not more than three conductors are in a conduit (Column 4). No adjustment factor for ambient temperature is needed as the temperature is 30°C (86°F).
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.