An electrician is installing a new 240 V, 30 A electric dryer in a residential basement. The dryer is located 2.5 m (8.2 ft) from the panelboard. What is the minimum size of copper conductor (NMD90 cable) required for this circuit, assuming the dwelling unit conductors meet the temperature limitations for 90 °C insulation?

For a 30 A circuit, Table 2 of the CEC indicates that a 10 AWG copper conductor is required for conductors having an insulation temperature rating of 90 °C (NMD

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is installing a new 240 V, 30 A electric dryer in a residential basement. The dryer is located 2.5 m (8.2 ft) from the panelboard. What is the minimum size of copper conductor (NMD90 cable) required for this circuit, assuming the dwelling unit conductors meet the temperature limitations for 90 °C insulation?

Answer options:

  • 14 AWG
  • 12 AWG ✅ 10 AWG
  • 8 AWG

Correct answer: 10 AWG

Explanation: For a 30 A circuit, Table 2 of the CEC indicates that a 10 AWG copper conductor is required for conductors having an insulation temperature rating of 90 °C (NMD90). While 12 AWG is rated for 20 A and 14 AWG for 15 A, 10 AWG provides the necessary ampacity for a 30 A load. 8 AWG would be oversized for this application.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.