An electrician is installing a single-phase, 240 V air conditioner unit on the roof of a commercial building. The unit has a nameplate rating of 35 A continuous load and a minimum circuit ampacity (MCA) of 44 A. What is the minimum size of overcurrent protection required for this unit, according to the CEC?
Rule 28-200 and related sections for motors and air conditioning equipment often specify that the overcurrent protection shall not exceed the manufacturer's spe
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is installing a single-phase, 240 V air conditioner unit on the roof of a commercial building. The unit has a nameplate rating of 35 A continuous load and a minimum circuit ampacity (MCA) of 44 A. What is the minimum size of overcurrent protection required for this unit, according to the CEC?
Answer options:
- 30 A
- 40 A ✅ 50 A
- 60 A
Correct answer: 50 A
Explanation: Rule 28-200 and related sections for motors and air conditioning equipment often specify that the overcurrent protection shall not exceed the manufacturer's specified MCA. Given an MCA of 44 A, the next standard size of overcurrent device above this would be 50 A.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.