Electrician Red Seal · Question
An electrician is inspecting an existing 120/208 V, 3-phase, 4-wire, 100 A service entrance in a community centre. The main service disconnect is located on the exterior wall. What is the maximum length allowed for the service conductors between the point of entry into the building and the main service disconnect switch, assuming the conductors are enclosed in rigid metal conduit?
CEC Rule 6-200(1) requires the service box (main service disconnect) to be located as close as practicable to the point where the service conductors enter the b
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is inspecting an existing 120/208 V, 3-phase, 4-wire, 100 A service entrance in a community centre. The main service disconnect is located on the exterior wall. What is the maximum length allowed for the service conductors between the point of entry into the building and the main service disconnect switch, assuming the conductors are enclosed in rigid metal conduit?
Answer options:
- No maximum length specified, provided fire spread is accounted for.
- 1.5 m (5 ft)
- 3 m (10 ft) ✅ As short as practicable, not exceeding 7.5 m (25 ft).
Correct answer: As short as practicable, not exceeding 7.5 m (25 ft).
Explanation: CEC Rule 6-200(1) requires the service box (main service disconnect) to be located as close as practicable to the point where the service conductors enter the building, or where they leave an embedded or enclosed raceway, and in no case shall the service conductors within the building exceed 7.5 m (25 ft) to the service box.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses