A construction site is powered by a temporary 120/208 V, 3-phase, 4-wire portable generator. What is the minimum size copper bonding conductor required to connect the generator's non-current-carrying metal parts to the frame of the generator, assuming the generator output is protected by a 100 A main circuit breaker?
According to CEC Table 16, for an overcurrent device rated at 100 A, the minimum size copper bonding conductor required is #2 AWG. This ensures that in the even
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A construction site is powered by a temporary 120/208 V, 3-phase, 4-wire portable generator. What is the minimum size copper bonding conductor required to connect the generator's non-current-carrying metal parts to the frame of the generator, assuming the generator output is protected by a 100 A main circuit breaker?
Answer options:
- #6 AWG
- #4 AWG ✅ #2 AWG
- #1/0 AWG
Correct answer: #2 AWG
Explanation: According to CEC Table 16, for an overcurrent device rated at 100 A, the minimum size copper bonding conductor required is #2 AWG. This ensures that in the event of a ground fault, sufficient current can flow to trip the 100 A overcurrent device.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.