An electrician is selecting conductors for a 50 hp, 575 V, 3-phase squirrel cage induction motor with a Code F design. According to the Canadian Electrical Code (CEC) Rule 28-106, what is the minimum ampacity required for the branch circuit conductors before applying any correction or adjustment factors?
CEC Table 44 provides full load currents for motors. For a 50 hp, 575 V, 3-phase motor, the full load current is 52 A. According to Rule 28-106(1), the minimum
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is selecting conductors for a 50 hp, 575 V, 3-phase squirrel cage induction motor with a Code F design. According to the Canadian Electrical Code (CEC) Rule 28-106, what is the minimum ampacity required for the branch circuit conductors before applying any correction or adjustment factors?
Answer options: ✅ 65 A
- 52 A
- 81 A
- 75 A
Correct answer: 65 A
Explanation: CEC Table 44 provides full load currents for motors. For a 50 hp, 575 V, 3-phase motor, the full load current is 52 A. According to Rule 28-106(1), the minimum conductor ampacity for a motor branch circuit is 125% of the motor's full load current. So, 52 A * 1.25 = 65 A.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.