An electrician is selecting conductors for a 50 hp, 575 V, 3-phase squirrel cage induction motor with a Code F design. According to the Canadian Electrical Code (CEC) Rule 28-106, what is the minimum ampacity required for the branch circuit conductors before applying any correction or adjustment factors?

CEC Table 44 provides full load currents for motors. For a 50 hp, 575 V, 3-phase motor, the full load current is 52 A. According to Rule 28-106(1), the minimum

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is selecting conductors for a 50 hp, 575 V, 3-phase squirrel cage induction motor with a Code F design. According to the Canadian Electrical Code (CEC) Rule 28-106, what is the minimum ampacity required for the branch circuit conductors before applying any correction or adjustment factors?

Answer options: ✅ 65 A

  • 52 A
  • 81 A
  • 75 A

Correct answer: 65 A

Explanation: CEC Table 44 provides full load currents for motors. For a 50 hp, 575 V, 3-phase motor, the full load current is 52 A. According to Rule 28-106(1), the minimum conductor ampacity for a motor branch circuit is 125% of the motor's full load current. So, 52 A * 1.25 = 65 A.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.