Electrician Red Seal · Question
A 230 V, 1-phase, 60 Hz motor requires a 40 microfarad (µF) start capacitor connected in series with the start winding. If the motor controller is replacing the start capacitor, which characteristic is critical for the new capacitor to ensure proper motor operation and prevent damage?
Start capacitors in single-phase motors often experience transient voltages higher than the AC line voltage (sometimes 2 to 3 times the line voltage) during the
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 230 V, 1-phase, 60 Hz motor requires a 40 microfarad (µF) start capacitor connected in series with the start winding. If the motor controller is replacing the start capacitor, which characteristic is critical for the new capacitor to ensure proper motor operation and prevent damage?
Answer options:
- Its voltage rating must be at least 230 V AC. ✅ Its voltage rating must be at least 460 V AC.
- Its capacitance must be exactly 40 µF.
- Its capacitance must be between 30 µF and 50 µF.
Correct answer: Its voltage rating must be at least 460 V AC.
Explanation: Start capacitors in single-phase motors often experience transient voltages higher than the AC line voltage (sometimes 2 to 3 times the line voltage) during the starting period. Therefore, the capacitor's voltage rating must be significantly higher than the line voltage, typically at least twice the RMS line voltage, to prevent failure.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.