An electrician is installing armoured cable (AC90) in a ceiling plenum space above a suspended ceiling where environmental air is handled. According to the Canadian Electrical Code (CEC), what specific precaution must be taken regarding the termination of the armoured cable?
Rule 12-610(5) and 12-902(1) in the CEC requires an insulating bushing (commonly called an anti-short bushing) to be installed between the conductors and the ar
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is installing armoured cable (AC90) in a ceiling plenum space above a suspended ceiling where environmental air is handled. According to the Canadian Electrical Code (CEC), what specific precaution must be taken regarding the termination of the armoured cable?
Answer options:
- The armoured cable must be run in rigid conduit for its entire length. ✅ An insulating bushing (anti-short bushing) is required at all armoured cable terminations.
- The armoured cable requires a continuous bond wire connecting all fixture boxes.
- The cable must be supported every 500 mm (20 in.) in the plenum.
Correct answer: An insulating bushing (anti-short bushing) is required at all armoured cable terminations.
Explanation: Rule 12-610(5) and 12-902(1) in the CEC requires an insulating bushing (commonly called an anti-short bushing) to be installed between the conductors and the armour at all terminations of armoured cable to protect the conductors from abrasion. While support and bonding are generally important, the specific precaution for terminations is the bushing.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.