Electrician Red Seal · Question
A journeyperson is performing phase rotation testing on a newly installed 600 V three-phase motor feeder before connecting it to the motor. They use a phase rotation meter and measure between the three phase conductors. The meter indicates a reverse phase rotation. What is the correct action to take to correct this situation?
To correct reverse phase rotation in a three-phase system, it is necessary to interchange any two of the three phase conductors. This changes the sequence appli
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A journeyperson is performing phase rotation testing on a newly installed 600 V three-phase motor feeder before connecting it to the motor. They use a phase rotation meter and measure between the three phase conductors. The meter indicates a reverse phase rotation. What is the correct action to take to correct this situation?
Answer options:
- Reverse the incoming line connections at the main breaker. ✅ Interchange any two of the three phase conductors at the motor or the supply end of the feeder.
- Change the overload settings in the motor starter.
- Add a capacitor bank to correct the phase angle.
Correct answer: Interchange any two of the three phase conductors at the motor or the supply end of the feeder.
Explanation: To correct reverse phase rotation in a three-phase system, it is necessary to interchange any two of the three phase conductors. This changes the sequence applied to the motor or load, causing it to operate in the desired direction. Reversing incoming lines at the main breaker affects the entire bus, which is typically not the correct approach for a single feeder, and overload settings or capacitor banks do not affect phase rotation.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.