A 75 kVA, single-phase transformer is connected to a 480 V primary supply. If the secondary voltage is 120 V, what is the rated full-load current on the secondary side?

The full-load current on the secondary side (I2) can be calculated using the formula Power (VA) = V2 * I2. Therefore, I2 = Power (VA) / V2 = 75,000 VA / 120 V =

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A 75 kVA, single-phase transformer is connected to a 480 V primary supply. If the secondary voltage is 120 V, what is the rated full-load current on the secondary side?

Answer options:

  • 156.25 A
  • 312.5 A
  • 433.0 A ✅ 625.0 A

Correct answer: 625.0 A

Explanation: The full-load current on the secondary side (I2) can be calculated using the formula Power (VA) = V2 * I2. Therefore, I2 = Power (VA) / V2 = 75,000 VA / 120 V = 625.0 A.