During a rough-in inspection, an electrician notices that NMD90 cable passing through a steel stud has had the protective bushing fall out. What specific CEC rule is violated by this condition?
Rule 12-510(1) mandates that non-metallic sheathed cable passing through metal studs must be protected from physical damage by means of a bushing or grommet. Th
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: During a rough-in inspection, an electrician notices that NMD90 cable passing through a steel stud has had the protective bushing fall out. What specific CEC rule is violated by this condition?
Answer options: ✅ Rule 12-510(1) - Protection against physical damage.
- Rule 12-516(2) - Cable support requirements.
- Rule 12-518(1) - Minimum bend radius.
- Rule 12-520(1) - Cable termination enclosures.
Correct answer: Rule 12-510(1) - Protection against physical damage.
Explanation: Rule 12-510(1) mandates that non-metallic sheathed cable passing through metal studs must be protected from physical damage by means of a bushing or grommet. The absence of this protection violates this rule.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.