During a rough-in inspection, an electrician notices that NMD90 cable passing through a steel stud has had the protective bushing fall out. What specific CEC rule is violated by this condition?

Rule 12-510(1) mandates that non-metallic sheathed cable passing through metal studs must be protected from physical damage by means of a bushing or grommet. Th

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: During a rough-in inspection, an electrician notices that NMD90 cable passing through a steel stud has had the protective bushing fall out. What specific CEC rule is violated by this condition?

Answer options: ✅ Rule 12-510(1) - Protection against physical damage.

  • Rule 12-516(2) - Cable support requirements.
  • Rule 12-518(1) - Minimum bend radius.
  • Rule 12-520(1) - Cable termination enclosures.

Correct answer: Rule 12-510(1) - Protection against physical damage.

Explanation: Rule 12-510(1) mandates that non-metallic sheathed cable passing through metal studs must be protected from physical damage by means of a bushing or grommet. The absence of this protection violates this rule.