An industrial electrician is installing a 3-phase, 480 V motor circuit using armoured cable (AC90). The cable passes through an area where it is exposed to potential mechanical damage. What is the minimum radius of the bend in the cable, measured to the inner edge, if the cable has an outside diameter of 30 mm?

Rule 12-608(1) of the CEC specifies that armoured cables (AC90) shall not be bent with a radius of the inner edge of the bend less than 8 times the outside diam

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An industrial electrician is installing a 3-phase, 480 V motor circuit using armoured cable (AC90). The cable passes through an area where it is exposed to potential mechanical damage. What is the minimum radius of the bend in the cable, measured to the inner edge, if the cable has an outside diameter of 30 mm?

Answer options:

  • 180 mm ✅ 240 mm
  • 150 mm
  • 120 mm

Correct answer: 240 mm

Explanation: Rule 12-608(1) of the CEC specifies that armoured cables (AC90) shall not be bent with a radius of the inner edge of the bend less than 8 times the outside diameter of the cable. For a cable with a 30 mm outside diameter, the minimum bend radius would be 8 * 30 mm = 240 mm.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.