A journeyperson is installing a 20 A, 120 V circuit for lighting in a commercial office. The circuit consists of two conductors plus ground and will be run in Electrical Metallic Tubing (EMT). According to the Canadian Electrical Code (CEC), what is the minimum trade size of EMT required for this installation if using 12 AWG T90 nylon conductors?
For two 12 AWG T90 nylon conductors, Table 9A of the CEC (allowing for two conductors) indicates that 16 mm (1/2 in.) EMT is sufficient. Larger sizes would prov
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A journeyperson is installing a 20 A, 120 V circuit for lighting in a commercial office. The circuit consists of two conductors plus ground and will be run in Electrical Metallic Tubing (EMT). According to the Canadian Electrical Code (CEC), what is the minimum trade size of EMT required for this installation if using 12 AWG T90 nylon conductors?
Answer options: ✅ 16 mm (1/2 in.)
- 21 mm (3/4 in.)
- 27 mm (1 in.)
- 35 mm (1 1/4 in.)
Correct answer: 16 mm (1/2 in.)
Explanation: For two 12 AWG T90 nylon conductors, Table 9A of the CEC (allowing for two conductors) indicates that 16 mm (1/2 in.) EMT is sufficient. Larger sizes would provide more capacity but are not the minimum requirement.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.