During an inspection of a newly installed data centre, it's observed that communication cables are run in the same tray as 600 V power conductors. The communication cables are rated for 300 V. According to CEC Rule 12-904, what action is required to ensure compliance?
CEC Rule 12-904(1)(b) states that communication and power cables operating at over 300 V shall not be installed in the same cable tray without a barrier of shee
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: During an inspection of a newly installed data centre, it's observed that communication cables are run in the same tray as 600 V power conductors. The communication cables are rated for 300 V. According to CEC Rule 12-904, what action is required to ensure compliance?
Answer options:
- No action is required as long as the trays are separated by at least 150 mm (6 in.).
- The communication cables must be moved to a separate cable tray. ✅ A barrier ofsheet steel or other approved material must be installed for the full length of the tray.
- Install higher voltage rated communication cables.
Correct answer: A barrier ofsheet steel or other approved material must be installed for the full length of the tray.
Explanation: CEC Rule 12-904(1)(b) states that communication and power cables operating at over 300 V shall not be installed in the same cable tray without a barrier of sheet steel or other approved material that is at least equivalent to the width of the tray.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.