A homeowner wants to install a new hot tub rated at 40 A, 240 V, single-phase, outside on a concrete pad. The electrician plans to run NMD90 cable from the main service panel in the basement through the exterior wall to a disconnect switch located 2 meters (6.5 feet) from the hot tub. What is the minimum conductor size required for this installation according to CEC Rule 68-060, assuming copper conductors?
CEC Rule 68-060(1)(a) requires that conductors supplying a pool, tub, or spa shall be copper of an ampacity not less than 125% of the rating of the branch circu
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A homeowner wants to install a new hot tub rated at 40 A, 240 V, single-phase, outside on a concrete pad. The electrician plans to run NMD90 cable from the main service panel in the basement through the exterior wall to a disconnect switch located 2 meters (6.5 feet) from the hot tub. What is the minimum conductor size required for this installation according to CEC Rule 68-060, assuming copper conductors?
Answer options:
- #10 AWG
- #8 AWG ✅ #6 AWG
- #4 AWG
Correct answer: #6 AWG
Explanation: CEC Rule 68-060(1)(a) requires that conductors supplying a pool, tub, or spa shall be copper of an ampacity not less than 125% of the rating of the branch circuit. For a 40 A load, 40 A × 1.25 = 50 A. From CEC Table 2, #6 AWG copper conductors with NMD90 insulation have an ampacity of 65 A, which is suitable. #8 AWG only has an ampacity of 50 A, which is not greater than 125% of the load.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.