A new disconnect switch is being installed for a 480 V, 3-phase motor. The visible blade type disconnect is rated for 60 A. What is the minimum clearance in front of the live parts of this disconnect switch, if it can be accessed from the front, according to CEC Table 1?
For equipment operating between 301 V and 750 V, CEC Table 1 requires a minimum clearance of 900 mm (3 ft.) in front of live parts where adequate working space
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A new disconnect switch is being installed for a 480 V, 3-phase motor. The visible blade type disconnect is rated for 60 A. What is the minimum clearance in front of the live parts of this disconnect switch, if it can be accessed from the front, according to CEC Table 1?
Answer options:
- 750 mm (30 in.) ✅ 900 mm (3 ft.)
- 1000 mm (3 ft. 3 in.)
- 1200 mm (4 ft.)
Correct answer: 900 mm (3 ft.)
Explanation: For equipment operating between 301 V and 750 V, CEC Table 1 requires a minimum clearance of 900 mm (3 ft.) in front of live parts where adequate working space is needed for maintenance and operation.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.