A Red Seal electrician is commissioned to install a new electric vehicle (EV) charging station in a detached garage. The charging station is rated at 40 A. What is the MINIMUM size, in AWG, of copper conductors required for this dedicated circuit, assuming an NMD90 cable and no other derating factors?

Rule 8-106(1) and 8-108(1) require a continuous load to be multiplied by 125%. So, 40 A * 125% = 50 A. According to Table 2 of the CEC, 6 AWG NMD90 copper condu

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A Red Seal electrician is commissioned to install a new electric vehicle (EV) charging station in a detached garage. The charging station is rated at 40 A. What is the MINIMUM size, in AWG, of copper conductors required for this dedicated circuit, assuming an NMD90 cable and no other derating factors?

Answer options:

  • 10 AWG
  • 8 AWG ✅ 6 AWG
  • 4 AWG

Correct answer: 6 AWG

Explanation: Rule 8-106(1) and 8-108(1) require a continuous load to be multiplied by 125%. So, 40 A * 125% = 50 A. According to Table 2 of the CEC, 6 AWG NMD90 copper conductors are rated for 60 A at 90°C, which is sufficient for a 50 A continuous load. Therefore, 6 AWG is the minimum for the circuit.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.