A Red Seal electrician is commissioned to install a new electric vehicle (EV) charging station in a detached garage. The charging station is rated at 40 A. What is the MINIMUM size, in AWG, of copper conductors required for this dedicated circuit, assuming an NMD90 cable and no other derating factors?
Rule 8-106(1) and 8-108(1) require a continuous load to be multiplied by 125%. So, 40 A * 125% = 50 A. According to Table 2 of the CEC, 6 AWG NMD90 copper condu
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A Red Seal electrician is commissioned to install a new electric vehicle (EV) charging station in a detached garage. The charging station is rated at 40 A. What is the MINIMUM size, in AWG, of copper conductors required for this dedicated circuit, assuming an NMD90 cable and no other derating factors?
Answer options:
- 10 AWG
- 8 AWG ✅ 6 AWG
- 4 AWG
Correct answer: 6 AWG
Explanation: Rule 8-106(1) and 8-108(1) require a continuous load to be multiplied by 125%. So, 40 A * 125% = 50 A. According to Table 2 of the CEC, 6 AWG NMD90 copper conductors are rated for 60 A at 90°C, which is sufficient for a 50 A continuous load. Therefore, 6 AWG is the minimum for the circuit.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.