A utility company's billing statement includes a power factor penalty. The facility has an average active power demand of 533.5 kW and an average power factor of 0.70 lagging. If the target power factor to avoid penalties is 0.90 lagging, what is the minimum additional reactive power (in kVAR) that needs to be supplied by power factor correction capacitors to meet the target PF, assuming the active power remains constant?
Active power (P) = 533.5 kW. Initial PF = 0.70 (θ1 = arccos(0.70) ≈ 45.57°, tan(θ1) ≈ 1.0202). Target PF = 0.90 (θ2 = arccos(0.90) ≈ 25.84°, tan(θ2) ≈ 0.4843).
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A utility company's billing statement includes a power factor penalty. The facility has an average active power demand of 533.5 kW and an average power factor of 0.70 lagging. If the target power factor to avoid penalties is 0.90 lagging, what is the minimum additional reactive power (in kVAR) that needs to be supplied by power factor correction capacitors to meet the target PF, assuming the active power remains constant?
Answer options:
- 153.1 kVAR
- 204.2 kVAR ✅ 285.9 kVAR
- 306.3 kVAR
Correct answer: 285.9 kVAR
Explanation: Active power (P) = 533.5 kW. Initial PF = 0.70 (θ1 = arccos(0.70) ≈ 45.57°, tan(θ1) ≈ 1.0202). Target PF = 0.90 (θ2 = arccos(0.90) ≈ 25.84°, tan(θ2) ≈ 0.4843). Initial reactive power (Q1) = P × tan(θ1) = 533.5 kW × 1.0202 ≈ 544.28 kVAR. Target reactive power (Q2) = P × tan(θ2) = 533.5 kW × 0.4843 ≈ 258.38 kVAR. The reactive power to be supplied by capacitors (ΔQ) = Q1 - Q2 = 544.28 kVAR - 258.38 kVAR = 285.9 kVAR.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.