What is the maximum allowable voltage drop permitted by the CEC for a feeder circuit?

CEC Rule 8-102 is an informational note, not a mandatory rule. It recommends a maximum of 3% voltage drop for feeders and 5% total from the supply to the point

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: What is the maximum allowable voltage drop permitted by the CEC for a feeder circuit?

Answer options:

  • 1%
  • 3%
  • 5% ✅ There is no mandatory maximum, only a recommendation.

Correct answer: There is no mandatory maximum, only a recommendation.

Explanation: CEC Rule 8-102 is an informational note, not a mandatory rule. It recommends a maximum of 3% voltage drop for feeders and 5% total from the supply to the point of utilization, but it is not an enforceable requirement unless specified by the local authority or project specs.