What is the maximum allowable voltage drop permitted by the CEC for a feeder circuit?
CEC Rule 8-102 is an informational note, not a mandatory rule. It recommends a maximum of 3% voltage drop for feeders and 5% total from the supply to the point
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: What is the maximum allowable voltage drop permitted by the CEC for a feeder circuit?
Answer options:
- 1%
- 3%
- 5% ✅ There is no mandatory maximum, only a recommendation.
Correct answer: There is no mandatory maximum, only a recommendation.
Explanation: CEC Rule 8-102 is an informational note, not a mandatory rule. It recommends a maximum of 3% voltage drop for feeders and 5% total from the supply to the point of utilization, but it is not an enforceable requirement unless specified by the local authority or project specs.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.