A 480V to 120/208V, 3-phase, delta-wye transformer has a kVA rating of 45. What is the full-load current on the secondary side?

The formula for full-load current in a 3-phase system is I = kVA / (V_line × √3). For the secondary, I = 45,000 VA / (208 V × 1.732) = 45,000 / 360.25 = 124.9 A

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A 480V to 120/208V, 3-phase, delta-wye transformer has a kVA rating of 45. What is the full-load current on the secondary side?

Answer options: ✅ 125 A

  • 216 A
  • 108 A
  • 62 A

Correct answer: 125 A

Explanation: The formula for full-load current in a 3-phase system is I = kVA / (V_line × √3). For the secondary, I = 45,000 VA / (208 V × 1.732) = 45,000 / 360.25 = 124.9 A, which is approximately 125 A.