A 480V to 120/208V, 3-phase, delta-wye transformer has a kVA rating of 45. What is the full-load current on the secondary side?
The formula for full-load current in a 3-phase system is I = kVA / (V_line × √3). For the secondary, I = 45,000 VA / (208 V × 1.732) = 45,000 / 360.25 = 124.9 A
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 480V to 120/208V, 3-phase, delta-wye transformer has a kVA rating of 45. What is the full-load current on the secondary side?
Answer options: ✅ 125 A
- 216 A
- 108 A
- 62 A
Correct answer: 125 A
Explanation: The formula for full-load current in a 3-phase system is I = kVA / (V_line × √3). For the secondary, I = 45,000 VA / (208 V × 1.732) = 45,000 / 360.25 = 124.9 A, which is approximately 125 A.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.