You need to install twelve #12 AWG RW90 copper conductors in a single EMT conduit. What is the minimum trade size of EMT required?
Using CEC Table 10A for the area of a #12 AWG RW90 conductor (13.79 mm²) and multiplying by 12 gives a total area of 165.48 mm². Using Table 9D for EMT and appl
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: You need to install twelve #12 AWG RW90 copper conductors in a single EMT conduit. What is the minimum trade size of EMT required?
Answer options:
- 1/2 inch
- 3/4 inch ✅ 1 inch
- 1 1/4 inch
Correct answer: 1 inch
Explanation: Using CEC Table 10A for the area of a #12 AWG RW90 conductor (13.79 mm²) and multiplying by 12 gives a total area of 165.48 mm². Using Table 9D for EMT and applying the 40% fill rule (for more than 2 conductors), a 3/4" EMT (max fill 137 mm²) is too small. A 1" EMT (max fill 225 mm²) is the correct minimum size.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.