What is the minimum size copper grounding conductor required for a service supplied by #3/0 AWG copper service conductors?
CEC Rule 10-812 and Table 17 dictate the size of the grounding conductor based on the size of the service conductors. For service conductors from #2 AWG up to #
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: What is the minimum size copper grounding conductor required for a service supplied by #3/0 AWG copper service conductors?
Answer options:
- #8 AWG ✅ #6 AWG
- #4 AWG
- #2 AWG
Correct answer: #6 AWG
Explanation: CEC Rule 10-812 and Table 17 dictate the size of the grounding conductor based on the size of the service conductors. For service conductors from #2 AWG up to #3/0 AWG copper, a #6 AWG copper grounding conductor is the minimum size required.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat