What is the minimum size copper grounding conductor required for a service supplied by #3/0 AWG copper service conductors?

CEC Rule 10-812 and Table 17 dictate the size of the grounding conductor based on the size of the service conductors. For service conductors from #2 AWG up to #

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: What is the minimum size copper grounding conductor required for a service supplied by #3/0 AWG copper service conductors?

Answer options:

  • #8 AWG ✅ #6 AWG
  • #4 AWG
  • #2 AWG

Correct answer: #6 AWG

Explanation: CEC Rule 10-812 and Table 17 dictate the size of the grounding conductor based on the size of the service conductors. For service conductors from #2 AWG up to #3/0 AWG copper, a #6 AWG copper grounding conductor is the minimum size required.