When calculating the ampacity of conductors in a raceway, if you have 8 current-carrying conductors, what derating factor must be applied according to CEC Table 5C?
CEC Table 5C specifies the correction factors for the number of conductors in a raceway. For 7 to 9 conductors, a derating factor of 0.70 (or 70%) must be appli
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: When calculating the ampacity of conductors in a raceway, if you have 8 current-carrying conductors, what derating factor must be applied according to CEC Table 5C?
Answer options:
- 0.90
- 0.80 ✅ 0.70
- 0.50
Correct answer: 0.70
Explanation: CEC Table 5C specifies the correction factors for the number of conductors in a raceway. For 7 to 9 conductors, a derating factor of 0.70 (or 70%) must be applied to the conductor's tabulated ampacity.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.