When calculating the ampacity of conductors in a raceway, if you have 8 current-carrying conductors, what derating factor must be applied according to CEC Table 5C?

CEC Table 5C specifies the correction factors for the number of conductors in a raceway. For 7 to 9 conductors, a derating factor of 0.70 (or 70%) must be appli

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: When calculating the ampacity of conductors in a raceway, if you have 8 current-carrying conductors, what derating factor must be applied according to CEC Table 5C?

Answer options:

  • 0.90
  • 0.80 ✅ 0.70
  • 0.50

Correct answer: 0.70

Explanation: CEC Table 5C specifies the correction factors for the number of conductors in a raceway. For 7 to 9 conductors, a derating factor of 0.70 (or 70%) must be applied to the conductor's tabulated ampacity.