A 10 hp, 575V, 3-phase squirrel cage induction motor has a nameplate full-load current (FLC) of 11A. What is the maximum permissible rating for its non-time-delay fuses?
According to CEC Table 29, the maximum rating for non-time-delay fuses for a squirrel cage motor is 300% of the FLC. Calculation: 11A * 3.00 = 33A. Since 33A is
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 10 hp, 575V, 3-phase squirrel cage induction motor has a nameplate full-load current (FLC) of 11A. What is the maximum permissible rating for its non-time-delay fuses?
Answer options:
- 15A
- 30A ✅ 35A
- 40A
Correct answer: 35A
Explanation: According to CEC Table 29, the maximum rating for non-time-delay fuses for a squirrel cage motor is 300% of the FLC. Calculation: 11A * 3.00 = 33A. Since 33A is not a standard fuse size, Rule 14-104 allows you to use the next higher standard size, which is 35A.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.