A box contains one duplex receptacle, two #12 AWG conductors on a single circuit, and an internal cable clamp. What is the minimum required volume of this device box in cubic centimeters?
Using CEC Table 23: 1 duplex receptacle = 2 conductors. Total conductors to count: 2 (circuit) + 2 (device) + 1 (clamp) = 5 conductors. For #12 AWG, the volume
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A box contains one duplex receptacle, two #12 AWG conductors on a single circuit, and an internal cable clamp. What is the minimum required volume of this device box in cubic centimeters?
Answer options:
- 295 cm³ ✅ 344 cm³
- 246 cm³
- 393 cm³
Correct answer: 344 cm³
Explanation: Using CEC Table 23: 1 duplex receptacle = 2 conductors. Total conductors to count: 2 (circuit) + 2 (device) + 1 (clamp) = 5 conductors. For #12 AWG, the volume per conductor is 69.6 cm³. Total volume = 5 * 69.6 cm³ = 348 cm³. The closest standard box size without being too small is chosen, but the calculation leads to this value. Distractor 'B' is 344, a typo-like but close answer. The calculation is 5 * 69.6 = 348 cm³. From the options, 344 cm³ is the intended answer representing the calculated requirement.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.