When connecting a solidly-grounded wye-connected system, where must the system neutral point be grounded?
CEC Rule 10-204 mandates that for an AC system that is required to be grounded, the grounding connection shall be made at the source of supply and not at any ot
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: When connecting a solidly-grounded wye-connected system, where must the system neutral point be grounded?
Answer options:
- At every device it connects to.
- Only at the last device in the circuit. ✅ Only at the source of supply.
- At both the source and the final load.
Correct answer: Only at the source of supply.
Explanation: CEC Rule 10-204 mandates that for an AC system that is required to be grounded, the grounding connection shall be made at the source of supply and not at any other point, except as specifically permitted elsewhere in the code.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.