Electrician Red Seal · Question
According to CEC Rule 10-204, where can the system bonding jumper be located?
CEC Rule 10-204 requires the system bonding jumper to be installed at the service box or at any subsequently connected distribution panel, where the neutral con
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: According to CEC Rule 10-204, where can the system bonding jumper be located?
Answer options:
- Only at the service box. ✅ At the service box or at a subsequently connected distribution panel.
- Only at the meter base.
- At the transformer secondary.
Correct answer: At the service box or at a subsequently connected distribution panel.
Explanation: CEC Rule 10-204 requires the system bonding jumper to be installed at the service box or at any subsequently connected distribution panel, where the neutral conductor is connected to ground.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.