A three-phase, 208V, 10 HP motor has a nameplate FLA of 30A. What is the minimum size of THHN conductor required for the motor circuit, assuming an ambient temperature of 30°C and no more than three current-carrying conductors in the conduit?
According to CEC Rule 28-106(1), continuous duty motor branch circuit conductors must have an ampacity not less than 125% of the motor's FLA. 125% of 30A is 37.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A three-phase, 208V, 10 HP motor has a nameplate FLA of 30A. What is the minimum size of THHN conductor required for the motor circuit, assuming an ambient temperature of 30°C and no more than three current-carrying conductors in the conduit?
Answer options:
- No. 12 AWG ✅ No. 10 AWG
- No. 8 AWG
- No. 6 AWG
Correct answer: No. 10 AWG
Explanation: According to CEC Rule 28-106(1), continuous duty motor branch circuit conductors must have an ampacity not less than 125% of the motor's FLA. 125% of 30A is 37.5A. From CEC Table 2 (using 75°C column for THHN as per 4-006(6)), No. 10 AWG copper conductor has an ampacity of 35A (for 60°C insulation, 40A for 75°C, 50A for 90°C). Due to the 125% factor, we need at least 37.5A. Checking Table 2 for 75°C (THHN), 10 AWG is 40A, which satisfies 37.5A. Therefore, No. 10 AWG is the minimum size.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.