A three-phase, 208V, 10 HP motor has a nameplate FLA of 30A. What is the minimum size of THHN conductor required for the motor circuit, assuming an ambient temperature of 30°C and no more than three current-carrying conductors in the conduit?

According to CEC Rule 28-106(1), continuous duty motor branch circuit conductors must have an ampacity not less than 125% of the motor's FLA. 125% of 30A is 37.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A three-phase, 208V, 10 HP motor has a nameplate FLA of 30A. What is the minimum size of THHN conductor required for the motor circuit, assuming an ambient temperature of 30°C and no more than three current-carrying conductors in the conduit?

Answer options:

  • No. 12 AWG ✅ No. 10 AWG
  • No. 8 AWG
  • No. 6 AWG

Correct answer: No. 10 AWG

Explanation: According to CEC Rule 28-106(1), continuous duty motor branch circuit conductors must have an ampacity not less than 125% of the motor's FLA. 125% of 30A is 37.5A. From CEC Table 2 (using 75°C column for THHN as per 4-006(6)), No. 10 AWG copper conductor has an ampacity of 35A (for 60°C insulation, 40A for 75°C, 50A for 90°C). Due to the 125% factor, we need at least 37.5A. Checking Table 2 for 75°C (THHN), 10 AWG is 40A, which satisfies 37.5A. Therefore, No. 10 AWG is the minimum size.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.