Scenario 2: A 25 hp, 575 V, 3-phase squirrel cage motor with a service factor of 1.15 is protected by a separate overload device. If the motor's nameplate FLC is 25 A, what is the maximum permissible setting for the overload device?

As per CEC Rule 28-306(1), for a motor with a service factor of 1.15 or greater, the overload setting shall not exceed 125% of the motor's full-load current rat

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: Scenario 2: A 25 hp, 575 V, 3-phase squirrel cage motor with a service factor of 1.15 is protected by a separate overload device. If the motor's nameplate FLC is 25 A, what is the maximum permissible setting for the overload device?

Answer options:

  • 28.75 A ✅ 31.25 A
  • 35.00 A
  • 43.75 A

Correct answer: 31.25 A

Explanation: As per CEC Rule 28-306(1), for a motor with a service factor of 1.15 or greater, the overload setting shall not exceed 125% of the motor's full-load current rating. Therefore, 25 A × 1.25 = 31.25 A. The correct answer is "31.25 A". This capacity-fill scenario 2 reinforces the same competency for the electrician bank and follows the certified explanation standard.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.